Hello,
Working on Symmetra SYAF16KXR9, I get a persistent RIM failure.
Removing this defective IM, the system return to normal but battery 02, 04, 06, 08, 10 and 12 are missing!
Is this normal or hiding an other defect?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:57 AM . Last Modified: 2024-03-18 01:05 AM
It is normal - each IM monitors half of the batteries. Once you add a functioning RIM in, it will see all of the batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:57 AM . Last Modified: 2024-03-18 01:05 AM
It is normal - each IM monitors half of the batteries. Once you add a functioning RIM in, it will see all of the batteries.