I reset the NMC2 AP9630 card to factory default, I have done the procedure by issue the command resetTodef –p all for two management cards.
After reboot, I found that I cannot use the ID: apc, pwd: apc to access card. (I try to refer manual, it mentions that ID and pwd shall be apc. )
I can use the ID: device, pwd: apc to access card, but the hostname is still inside the card.
May I know any step I can access back the card with administrator ID? Also how to perform card reset as factory default?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:52 AM . Last Modified: 1 month ago
Hi Wing,
Forgive me but can you give me the specific numbers? Many people tell me "the latest" which is their honest thought but it truly is not.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:52 AM . Last Modified: 1 month ago
What firmware version is on the AP9630?
It sounds like you experienced this issue here which has been fixed in more recent firmware versions -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA175980
The article will give you instructions on how to proceed. I recommend reviewing the article and towards the end it will explain your options. If you're local to the card, I would suggest doing the 'format' option.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:52 AM . Last Modified: 1 month ago
On 17/11/2015 2:28 AM, Angela said:What firmware version is on the AP9630?
It sounds like you experienced this issue here which has been fixed in more recent firmware versions -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA175980
The article will give you instructions on how to proceed. I recommend reviewing the article and towards the end it will explain your options. If you're local to the card, I would suggest doing the 'format' option.
Good day Angela.
The firmware version should be a latest version.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:52 AM . Last Modified: 1 month ago
Hi Wing,
Forgive me but can you give me the specific numbers? Many people tell me "the latest" which is their honest thought but it truly is not.
Thanks!