Problem with Galaxy 3000
Hello everyone.
I had a problem with my Galaxy system.
when performing test, the system changed from battery operation to normal operation but the EMI Board blew up completly. Several varistor were damaged.
My question is about if it is necessary (or even mandatory) to put the neutral in the input, and if this may be cause for the EMI boatd to blow? The manual says that it is recommended to have a Wye transfo (but no mandatory). The system has no transfo neither the input nor the output. Is it also necessary to check the phase sequence?
Besides, for monitoring the Galaxy 3000 from a DCS, what options do I have?