I wonder if anyone can help with my query.
I have a SUM1500RMXLI2U which has the following kit plugged into it:
The majority of the time the TFT monitor is switched off. When it is off the load status shows as 0%. When it is on it shows 5% load in the load status.
The physical UPS load indicator shows no lit lights. I'm guessing each one represents approx 20% load?
I can see from my HP Management software that the HP server is using 35W.
I'm not sure of the other equipment.
Will the load status only show a value when 5% or more load is used? Or shoudl I be seeing a couple of percent with the other equipment being on?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:43 AM . Last Modified: 2024-02-29 10:35 PM
Thanks Bill, that has confirmed my hunch that the load is not big enough until the monitor is switched on. I may plug both server PSU's into the UPS to see if that registers a change.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:35 PM
Liam,
PowerChute will report the information the UPS provides. Below is a screenshot of PowerChute Business Edition Agent 9.2 attached to a SMX1500. The load displayed on the UPS LCD is 3% and PowerChute is displaying 3.1%
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:43 AM . Last Modified: 2024-02-29 10:35 PM
Liam,
With a SUA Smart-UPS with that light of a load the UPS may not report it accurately. I ran a few tests with PowerChute Agent 9.0.3 and APCUPSD attached to SUA1500. Unless I put a 45 watt load or greater on the UPS both of the applications reported zero load.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:43 AM . Last Modified: 2024-02-29 10:35 PM
Thanks Bill, that has confirmed my hunch that the load is not big enough until the monitor is switched on. I may plug both server PSU's into the UPS to see if that registers a change.