Hello.
1. I have Physical Server on which Vcenter is running . I've installed here /Windows 2008r2/ Powerchute Network Shutdown. Enabled VM support, and not tick Vcenter is VM ofcourse /it is physical/ and configured rest (Vms shutdown, times etc)
Question.
I don't know if Powerchute is smart enough 🙂 When VMs are down. Powerchute will shut down Windows 2008r2 /where vcenter is running).?
I didn't add this physical server in powerchute it was not option.
I think powerschute is smart and it shutdown physical server - Windows 2008r2 because Vcenter is running on it ? Am I right ?
2. I don't know does powerchute shut down ESXi hosts when all VMs are down ? /Enter ESXi hosts in maintance mode and shut it down ? /
/Sorry for poor English/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:58 AM . Last Modified: 2024-03-13 12:13 AM
Hi,
The PowerChute Network Shutdown 4.2 VMware User's Guide lists your configuration and describes how the process works on page 91.
PowerChute will shutdown the system vCenter Server is running on.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:58 AM . Last Modified: 2024-03-13 12:13 AM
Hi,
The PowerChute Network Shutdown 4.2 VMware User's Guide lists your configuration and describes how the process works on page 91.
PowerChute will shutdown the system vCenter Server is running on.