Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 11/9/2010
Greetings,
I am new here, but have been using PowerChute Network Shutdown for years. Today, I have encountered my first real stumper.
I work for a school district, and we have APC UPS's at nearly every school in our district (37) with Network Management Cards. Each site runs a VMware ESX 4.0 server with 3 or 4 virtual servers. In most cases, the VMs are one Windows 2008 server, one NetWare 6.5 server, and one SuSE Linux Enterprise Server (SLES) 10 server.
At one specific site, the NetWare and Windows servers have no problem communicating with the management card, but the SLES server keeps giving me "PowerChute cannot communicate with the Management Card" in the Events. When I installed PCNS, it registered with the NMC without any trouble, and the IP address of the VM showed up under "Clients" in the NMC's web management interface. I have uninstalled and reinstalled several times, each time making absolutely sure that my username, password, authentication phrase, IP address, and subnet mask are correct. The firewall is completely disabled on the SLES VM. I have upgraded to the latest firmware on the NMC (3.7.2; it had been at 3.5.5). I have tried deleting and manually re-adding the client IP through the NMC's management interface. I have not encountered any problems with PCNS under SLES at any other site; just this one.
I am not sure what else to check. Any suggestions?
Thanks! With much appreciation,
Bryce Newall
Systems Administrator
Poway Unified School District
Posted: 2021-06-30 07:54 PM
This was originally posted on APC forums on 8/29/2020
I had a similar issue when using the PCNS VM under VMware.
I was able to ping both ways between the PCNS VM and the NMC.
Connection would establish, but at the registration phase I'd get the message "PowerChute is not receiving data from the Network Management Card".
I found what the issue was in my case: due to some network changes I needed to change the IP address of the PCNS VM. I used nmtui to do this. The issue is that you must enter the IP address along with the subnet mask. ie. I enter x.x.x.x instead of x.x.x.x/24 . However, I only entered x.x.x.x . Hence it was my error, but the interface should have been a bit more idiot proof. It should have either not accepted the entry without the /xx , or it should have had a separate subnet mask field.
This probably won't help the OP, but may help others.
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 7/12/2011
I am having the same issue.
After the 2.2.4 powerchute installs, it registers the IP with the NMC, but it still say cannon communicate with the NMC when you check the powerchute page.
I have used firebind, and port 3052 is open
Posted: 2021-06-30 07:53 PM
This reply was originally posted by Angela on APC forums on 12/1/2010
yes, i agree. strange.i personally dont have any more ideas :-(. havent used SLES in some time and even so, this is beyond me.
Posted: 2021-06-30 07:53 PM
This reply was originally posted by Angela on APC forums on 11/9/2010
when it cannot maintain communication but registers successfully, it makes me think that this a port issue.
here are the ports:
NMC ->PCNS for shutdown command, any other communication: TCP 3052
NMC and PCNS maintaining communication: UDP 3052
PCNS->NMC: TCP/UDP 80 (or whatever port the HTTP (not HTTPS) port is set to on the NMC)
it sounds like something may be blocking UDP 3052 so that they cannot maintain communication after registering.
is there anyway you can verify/deny that this is the case? maybe temporarily disable the firewall on SLES and if that works, we can configure it to allow the aforementioned port? all ports above should be enabled for bi-directional communication. i find that temporarily disabling any firewall will save us sometime rather than trying to allow it first, so we can verify its definitely the issue.
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 11/9/2010
Hi, thanks for your response.
I don't think it's a firewall issue. I mentioned in my original message that the SLES firewall is completely disabled. I should have said that it is permanently disabled. I didn't just disable it to try to troubleshoot this issue; I disabled it during installation, and verified through YaST that it is still disabled. (For what we use the server for, we don't need it.)
That being said, is there a way to test connectivity to UDP ports from a SLES machine? Testing TCP is easy, but I don't know how to test UDP.
Thanks!
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 11/10/2010
>
I don't think it's a firewall issue.
>
You're probably right. I believe SLES 10 runs a 2.6 kernel with iptables built-in, so we can check for any firewall rules by issuing:
sudo iptables -L
If there are no rules, we should see something like:
voidstar@seaquest2:~$ sudo iptables -L
Chain INPUT (policy ACCEPT)
target prot opt source destination
Chain FORWARD (policy ACCEPT)
target prot opt source destination
Chain OUTPUT (policy ACCEPT)
target prot opt source destination
That being said, is there a way to test connectivity to UDP ports from a SLES machine? Testing TCP is easy, but I don't know how to test UDP.sudo netstat -an|grep "3052"
You can also see which process is listening on that port (PCNS or something else)sudo lsof -n|grep "3052"
Posted: 2021-06-30 07:53 PM
This reply was originally posted by Angela on APC forums on 11/9/2010
hi - sorry about that. i did miss that part so i apologize.
only thing that comes to mind is a port scanner. is there an online port scanner you can try to check with? i guess it'd have to be one that allows you to try and probe a specific port.
we see these issues commonly and it generally ends up being a port issue so that is why i suggested it. is this VM bridged directly to the same network as the NMC? i assume so. i would say its something on the network possibly blocking the traffic but you do have other devices working so that is not likely.
what do you think about a port scanner? for open ports we usually try to check with the netstat command - does SLES have that? it shows open ports but i thought it'd be the active ports.
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 11/16/2010
Hi, sorry for the delay; I got swept up in a couple of other projects and am just now getting back to this.
I haven't figured out how to quote a message to be able to reply to specific points, but I'll answer voidstar's suggestions here:
I ran "iptables -L" and the output was exactly as you showed, i.e. there are no rules.
netstat -an|grep "3052" produced the following output:
tcp 0 0 0.0.0.0:3052 0.0.0.0:* LISTEN
udp 0 0 0.0.0.0:3052 0.0.0.0:*
lsof -n|grep "3052" produced the following output:
java 8970 root 5u IPv4 312152 UDP *:apc-3052
java 8970 root 7u IPv4 312564 TCP *:apc-3052 (LISTEN)
It looks to me like only PCNS is using port 3052. I'll have to talk with someone else here about using Wireshark (we do have it), since I'm not familiar with how to use it.
Thanks!
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 12/1/2010
Hello again,
Well, I figured out how to work Wireshark! (Go me...) I'm having it do a packet capture filtering for UDP port 3052. About once every 25-26 seconds, I'm seeing a packet originating from the NMC's IP address, and the destination IP is the broadcast address. That's ALL I'm seeing; no UDP traffic originating from the servers. I also tried expanding the filter to include both UDP and TCP traffic searching for Port 3052, and all I get is that same packet every 25-26 seconds.
Any ideas where to go from here?
Thanks!
-- Bryce
Posted: 2021-06-30 07:53 PM
This reply was originally posted by Angela on APC forums on 12/1/2010
well i can tell you that packet is normal. that is the packet PCNS looks for to maintain communication with the network management card.so if you're seeing that, the NMC is doing what it is supposed to..
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 12/1/2010
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 12/1/2010
Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 12/1/2010
>
I think what may help me is to have a better understanding of how the NMC and the PowerChute clients communicate. \[...\] I'm seeing the periodic broadcasts FROM the NMC, but nothing going TO the NMC, even from the machines that are working properly, even when I first start the service. \[...\] This makes it sound to me like the NMC is the one doing all of the work, i.e. the PowerChute clients just sit there and listen for the periodic broadcasts, and if they don't get one after about 2 minutes, then they log that "PowerChute cannot communicate with the Management Card" error. Does that sound about right? \[...\] It seems that the only work done by the PowerChute client is the initial registration with the NMC during installation, which was successful.
>
That's correct. PowerChute initiates a connection to the NMC to register with it and to start a UPS shutdown. During normal operation, it monitors the NMC's periodic status updates.
So we know that the VM delivers packets to the SLES machine based on the wireshark results. We know that there's no firewall rules on the SLES machine. We could have a little more confidence that a userspace program can see the packets by running
nc -l -u -p 3052
and seeing if the packets show up, but I'll assume this works. We know that powerchute is running and is listening on the correct port.Posted: 2021-06-30 07:53 PM
This was originally posted on APC forums on 12/1/2010
nc -l -u -p 3052
and seeing if the packets show up, but I'll assume this works. We know that powerchute is running and is listening on the correct port.Posted: 2021-06-30 07:54 PM
This was originally posted on APC forums on 12/2/2010
>
However, netcat did NOT register any subsequent packets, even though Wireshark saw them. An even more interesting development is that if I pressed ENTER in the terminal window while netcat was running (which shouldn't do anything), Wireshark detected a malformed packet originating FROM the SLES machine, with a destination address of the NMC. Weird
>
That's just how netcat works... it receives the first packet and sends anything you type back.
Posted: 2021-06-30 07:54 PM
This was originally posted on APC forums on 12/2/2010
Posted: 2021-06-30 07:54 PM
This was originally posted on APC forums on 12/6/2010
"is there a way to test connectivity to UDP ports from a SLES machine? Testing TCP is easy, but I don't know how to test UDP."
If you're trying to see if a port is being blocked by an intervening firewall, you can use firebind.com. There is a java client that allows you to choose TCP or UDP, and any port (or range) from 1-65535. It then sends packets back and forth from your machine to the firebind server on the internet on the chosen ports, thereby verifying if there is an intervening firewall block or not. They have a javascript client too but it's TCP only and it's subject to some port restrictions due to browser limitations.
It's not a port scanner (since a port scanner would scan open ports on a target machine.) Instead it's a path (to the Internet) scanner.
http://www.firebind.com
- ProtocolGeek
Posted: 2021-06-30 07:54 PM
This reply was originally posted by Angela on APC forums on 12/6/2010
you are receiving top tier APC support forum the forum to be honest with you. phone support will most likely escalate it to the folks that already post on this board.
Posted: 2021-06-30 07:54 PM
This was originally posted on APC forums on 4/13/2011
Greetings,
This topic got back-burnered for a while, but I'm finally getting back to it.
Strangely, one of the two sites that I was having problems with mysteriously started working. I have no idea what was done; nothing that I did! Anyway, my original site still isn't working.
I tried running Firebind, as suggested by another user here. I'm not sure I know exactly what I'm doing, but here's what I did:
Chose Port 3052 as the outbound port.
Chose UDP as the protocol.
Clicked "Start".
The results are as follows:
================================
Firebind Port Test Results
Ports: 3052
Start time: Wed Apr 13 16:47:37 PDT 2011
End time:Wed Apr 13 16:47:38 PDT 2011
Duration: 0 seconds
Port Detail:
Passed: 3052
For more information visit http://www.firebind.com
================================
Anything else I can check?
Thanks!
Posted: 2021-06-30 07:54 PM
This was originally posted on APC forums on 8/29/2020
I had a similar issue when using the PCNS VM under VMware.
I was able to ping both ways between the PCNS VM and the NMC.
Connection would establish, but at the registration phase I'd get the message "PowerChute is not receiving data from the Network Management Card".
I found what the issue was in my case: due to some network changes I needed to change the IP address of the PCNS VM. I used nmtui to do this. The issue is that you must enter the IP address along with the subnet mask. ie. I enter x.x.x.x instead of x.x.x.x/24 . However, I only entered x.x.x.x . Hence it was my error, but the interface should have been a bit more idiot proof. It should have either not accepted the entry without the /xx , or it should have had a separate subnet mask field.
This probably won't help the OP, but may help others.