Good morning
I have installed PowerChute Business Edition V10.0.1.301 for Windows.
The timeout is just too short - logs off after 10 minutes or so. How can I change that?
I do appreciate your help. Thank you very much.
Marcos
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:48 AM
Dear Bill
I cannot thank you enough. I followed your instructions and now I have a much longer timeout.
Very much appreciated.
Kind regards
Marcos
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:49 AM
Hi,
Go to C:\Program Files (x86)\APC\PowerChute Business Edition\agent\etc and save the file webdefault.xml to Saved-webdefault.xml Once the file has been saved open webdefault.xml with a text editor. Search for the line session-timeout.
Change the line
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:58 AM . Last Modified: 2024-03-08 03:48 AM
Dear Bill
I cannot thank you enough. I followed your instructions and now I have a much longer timeout.
Very much appreciated.
Kind regards
Marcos