PowerChute Personal & multiple APC UPSs

Solved
FuzzyBunny_apc
Cadet
0 Likes
1
206

PowerChute Personal & multiple APC UPSs

This was originally posted on APC forums on 11/15/2016


I have two UPSs, one on my home PC which I monitor with PowerChute Personal and one remote UPS (Back-Ups XS 900) for my network gear which I would also like to monitor.  I had planned to use a USB over ethernet hub to connect the remote UPS to my network so I can see it from my home PC (if anyone has done that successfully please let me know) but what about PowerChute?  Is there an edition that is capable of monitoring and managing more than one APC UPS?

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
207

Re: PowerChute Personal & multiple APC UPSs

This reply was originally posted by Bill on APC forums on 11/18/2016


Hi,

We do not specifically support shutting down multiple machines with PowerChute Personal Edition however another forum did post a solution.

http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/13064/shutdown-multiple-devic...

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
208

Re: PowerChute Personal & multiple APC UPSs

This reply was originally posted by Bill on APC forums on 11/18/2016


Hi,

We do not specifically support shutting down multiple machines with PowerChute Personal Edition however another forum did post a solution.

http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/13064/shutdown-multiple-devic...