Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79125members
343521posts

PowerChute Business Edition and Hyper-V Core 2016?

KemarRoach
Cadet
0 Likes
1
150

PowerChute Business Edition and Hyper-V Core 2016?

I installed PowerChute (10.x) on the server core. It found the UPS and the Agent service runs fine. Now I try to (remotely) connect to the agent using a web browser https://:6547, but to no avail. Doesn't make a difference if I use the FQDN or IP-address. Restarted the Agent service a couple of times, but nope. Performed netstat -a and notice the localhost (0.0.0.0) is listening on port 6547, but it's not listening on the core's IP-address. Removed and re-installed the software, but that doesn't make a difference. How to get things going?

Tags (1)
1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
123

Re: PowerChute Business Edition and Hyper-V Core 2016?

@KemarRoach 

 

That is the correct output 

Netstat Return.png

 

You should check the firewall rules. Open PowerShell and run the command get-netfirewallrule -displayname "PowerChute Business Edition Agent"

The profile should be enabled, the profile public, and action should be allow.

PCBE Firewall Rules Output via Powershell.png

 

If you need to make a change to the firewall rule see https://docs.microsoft.com/en-us/powershell/module/netsecurity/set-netfirewallrule?view=windowsserve...

Tags (1)