PowerChute Business Edition and Hyper-V Core 2016?

KemarRoach
Cadet
0 Likes
1
162

PowerChute Business Edition and Hyper-V Core 2016?

I installed PowerChute (10.x) on the server core. It found the UPS and the Agent service runs fine. Now I try to (remotely) connect to the agent using a web browser https://:6547, but to no avail. Doesn't make a difference if I use the FQDN or IP-address. Restarted the Agent service a couple of times, but nope. Performed netstat -a and notice the localhost (0.0.0.0) is listening on port 6547, but it's not listening on the core's IP-address. Removed and re-installed the software, but that doesn't make a difference. How to get things going?

Tags (1)
1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
135

Re: PowerChute Business Edition and Hyper-V Core 2016?

@KemarRoach 

 

That is the correct output 

Netstat Return.png

 

You should check the firewall rules. Open PowerShell and run the command get-netfirewallrule -displayname "PowerChute Business Edition Agent"

The profile should be enabled, the profile public, and action should be allow.

PCBE Firewall Rules Output via Powershell.png

 

If you need to make a change to the firewall rule see https://docs.microsoft.com/en-us/powershell/module/netsecurity/set-netfirewallrule?view=windowsserve...