Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80824members
346893posts

Power view and new UPS Smart RT "D" Series

Solved
BillP
Administrator Administrator
Administrator
0 Likes
2
120

Power view and new UPS Smart RT "D" Series

This question was originally posted by Federico on APC forums on 4/19/2010


Old UPS models such as: SURT1000XLI, SURT2000XLI, SURT3000XLI and SURT5000XLI supported PowerView.

New models such as SURTD3000XLI and SURTD5000XLI came with no COM output port just a serial RJ45 Adaptor to COM. The thing is that PowerView doesn't work out of the box with this new "D" models.

Is there any way to make it work?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
120

Re: Power view and new UPS Smart RT "D" Series

This reply was originally posted by Federico on APC forums on 4/29/2010


I finally proved it won't work. APC forgot about PowerView with this usless "Digital" refresh. I wonder why the do this "updates" instead of shipping standard the hardwiring i/o kit...

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
120

Power view and new UPS Smart RT "D" Series

This reply was originally posted by Federico on APC forums on 4/19/2010


Old UPS models such as: SURT1000XLI, SURT2000XLI, SURT3000XLI and SURT5000XLI supported PowerView.

New models such as SURTD3000XLI and SURTD5000XLI came with no COM output port just a serial RJ45 Adaptor to COM. The thing is that PowerView doesn't work out of the box with this new "D" models.

Is there any way to make it work?

BillP
Administrator Administrator
Administrator
0 Likes
0
121

Re: Power view and new UPS Smart RT "D" Series

This reply was originally posted by Federico on APC forums on 4/29/2010


I finally proved it won't work. APC forgot about PowerView with this usless "Digital" refresh. I wonder why the do this "updates" instead of shipping standard the hardwiring i/o kit...