Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-30 05:13 AM
This was originally posted on APC forums on 10/22/2008
I have a SU700xl that I've put a new battery in it. I do not have software, but I do have an AP9605 card. Is it possible to update the date that the battery was changed? Would that be something done via a "set" in SNMP?
Posted: 2021-06-30 05:13 AM
This was originally posted on APC forums on 10/22/2008
I tested with another unit and figured it out via an snmp set. I think I had tried it before on a different unit and didn't get it to work. thanks for the help
Posted: 2021-06-30 05:13 AM
This was originally posted on APC forums on 10/22/2008
I haven't sent the unit I'm working on now out to a terminal just yet, so for now i'm communicating via serial. My issue, I cannot find the option in the menus to make this change.
Posted: 2021-06-30 05:13 AM
This reply was originally posted by Angela on APC forums on 10/22/2008
do you have the IP address of this? you should be able to telnet to it. i dont have one to test but see if you get access via telnet and can do it that way.
if it doesnt have an IP, you would need a UPS serial cable (940-0024 or 940-1524) to configure the card with an IP.
if you cant do it via telnet, we should be able to find the OID to do a set.
User | Count |
---|---|
4835 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.