Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79384members
344124posts

Possible to change "battery change date" w/ AP9605?

Solved
cernst_apc
Ensign
Ensign
0 Likes
4
178

Possible to change "battery change date" w/ AP9605?

This was originally posted on APC forums on 10/22/2008


I have a SU700xl that I've put a new battery in it. I do not have software, but I do have an AP9605 card. Is it possible to update the date that the battery was changed? Would that be something done via a "set" in SNMP?


Accepted Solutions
cernst_apc
Ensign
Ensign
0 Likes
0
178

Re: Possible to change "battery change date" w/ AP9605?

This was originally posted on APC forums on 10/22/2008


I tested with another unit and figured it out via an snmp set. I think I had tried it before on a different unit and didn't get it to work. thanks for the help

See Answer In Context

4 Replies 4
cernst_apc
Ensign
Ensign
0 Likes
0
178

Re: Possible to change "battery change date" w/ AP9605?

This was originally posted on APC forums on 10/22/2008


I haven't sent the unit I'm working on now out to a terminal just yet, so for now i'm communicating via serial. My issue, I cannot find the option in the menus to make this change.

BillP
Administrator Administrator
Administrator
0 Likes
0
178

Re: Possible to change "battery change date" w/ AP9605?

This reply was originally posted by Angela on APC forums on 10/22/2008


i will attach the manual i have to this post.

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
178

Re: Possible to change "battery change date" w/ AP9605?

This reply was originally posted by Angela on APC forums on 10/22/2008


do you have the IP address of this? you should be able to telnet to it. i dont have one to test but see if you get access via telnet and can do it that way.

if it doesnt have an IP, you would need a UPS serial cable (940-0024 or 940-1524) to configure the card with an IP.

if you cant do it via telnet, we should be able to find the OID to do a set.

cernst_apc
Ensign
Ensign
0 Likes
0
179

Re: Possible to change "battery change date" w/ AP9605?

This was originally posted on APC forums on 10/22/2008


I tested with another unit and figured it out via an snmp set. I think I had tried it before on a different unit and didn't get it to work. thanks for the help