Posted: 2022-01-24 11:37 PM
Hi,
Is there any "official" document saying that PDU firmware upgrade will not/never swtich output during/after upgrade process ?
thanks.
Posted: 2022-01-25 05:30 AM
Hi
This subject has been discussed in a previous, that you can find here -> https://community.exchange.se.com/t5/EcoStruxure-IT-forum/Do-firmware-updates-require-reboots/td-p/2...
The short version is:
"For any devices, including Rack PDU, as long as they are operating normally and you have no active alarms we should check prior, a firmware upgrade of the management interface done through any method, including DCE, will not power on/off any attached loads."
But, as discussed in the post, there are fault states, that when active in the PDU, can cause the PDU to stop delivering power.
Best regards
Tonny
Posted: 2022-01-31 11:15 AM . Last Modified: 2022-01-31 11:16 AM
Thanks your answer.
So, why not writing an official document saying same thing ??