Posted: 2021-06-29 08:53 AM
This was originally posted on APC forums on 7/25/2017
Posted: 2021-06-29 08:53 AM
This reply was originally posted by Bill on APC forums on 7/25/2017
Hi,
You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration.
Posted: 2021-06-29 08:53 AM
This reply was originally posted by Bill on APC forums on 7/25/2017
Hi,
You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration.
Posted: 2021-06-29 08:53 AM
This was originally posted on APC forums on 8/15/2017
Hi,
thank you for your quick response.
We now deployed a seperate PCNS Appliance for every site without physical hosts and a PCNS Client with VMware Support for every site that has a physical host.
Unfortunately I wont have the chance to test the deployment soon.
But I will report the outcome when tests have been made.
Kind Regards