Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-29 08:53 AM
This was originally posted on APC forums on 7/25/2017
Posted: 2021-06-29 08:53 AM
This reply was originally posted by Bill on APC forums on 7/25/2017
Hi,
You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration.
Posted: 2021-06-29 08:53 AM
This reply was originally posted by Bill on APC forums on 7/25/2017
Hi,
You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration.
Posted: 2021-06-29 08:53 AM
This was originally posted on APC forums on 8/15/2017
Hi,
thank you for your quick response.
We now deployed a seperate PCNS Appliance for every site without physical hosts and a PCNS Client with VMware Support for every site that has a physical host.
Unfortunately I wont have the chance to test the deployment soon.
But I will report the outcome when tests have been made.
Kind Regards
User | Count |
---|---|
4835 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.