PCNS shuts down all hosts instead of two

Solved
DotB_apc
Cadet
0 Likes
2
94

PCNS shuts down all hosts instead of two

This was originally posted on APC forums on 7/25/2017


PCNS shuts down all hosts instead of two

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
95

Re: PCNS shuts down all hosts instead of two

This reply was originally posted by Bill on APC forums on 7/25/2017


Hi,

You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration. 

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
96

Re: PCNS shuts down all hosts instead of two

This reply was originally posted by Bill on APC forums on 7/25/2017


Hi,

You will find a description of how to configure PCNS for multiple sites in Application Note 180. The recommendation is to have PCNS running on a stand alone Windows system at each site. vCenter Server should also be running on a stand alone Windows system at one of the four sites. PCNS and vCenter can be running as VMs but that is not the recommended configuration. 

DotB_apc
Cadet
0 Likes
0
95

Re: PCNS shuts down all hosts instead of two

This was originally posted on APC forums on 8/15/2017


Hi,

thank you for your quick response.

We now deployed a seperate PCNS Appliance for every site without physical hosts and a PCNS Client with VMware Support for every site that has a physical host.

Unfortunately I wont have the chance to test the deployment soon.

But I will report the outcome when tests have been made.

Kind Regards