Posted: 2021-06-29 11:23 PM
This was originally posted on APC forums on 11/16/2017
We needed to switch the UPS from a power strip unit to a building wall outlet to see if it would remove Site Wiring Fault messages appearing in the APC logs..
When we unplugged the UPS from the power strip and connected to the wall, PCNS started to shut down the VMs and the host.
I am m not sure why, because it was on battery for about 4 seconds then back to building power via the wall outlet. So I am not sure why PCNS received an alert and PCNS did the shutdown?
The NMC Shutdown Settings are............
Shutdown:
Low Battery Duration 15 min
Max Required Delay 6 Min
Basic Low Battery Duration 600 sec
Duration of Shutdown
Sleep 0.0 hours
Sync Control Shut:
Shutdown Delay 600 sec
Return Delay 10 sec
NMC status of the batteries shows there is 24 minutes of run time remaining.
PCNS Events are only set to log events.
Below are some of the messages seen in the log
10:15:22 Low Battery Condition occurred
10:15:22 Shutdown Sequence Started on ESXi
10:15:23 Low Battery Condition Solved
10:15:24 UPS Critical: Low Battery resolved on host ESXi
10:15:24 Starting Maintenance Mode task on host ESXi
10:15:24 Shutting Down VMs
10:15:26 UPS no longer running on battery power or output power has been turned on
10:15:40 Battery is discharged
10:15:56 Battery has charged
10:16:17 Battery is discharged
10:16:21 Battery has recharged
Posted: 2021-06-29 11:23 PM
This reply was originally posted by Bill on APC forums on 12/14/2017
Hi,
I cannot say for sure but it is possible by disrupting ground the UPS reported the wrong runtime momentarily.
Posted: 2021-06-29 11:23 PM
This reply was originally posted by Bill on APC forums on 11/16/2017
Hi,
The log show that the UPS reported a low battery state at 10:15:22 so PCNS started the shut down process. A low battery event is treated as a critical event so by default PowerChute will trigger a shutdown sequence. Even though the event cleared a second later the shutdown cannot be disabled for this events to prevent catastrophic system failure.
Posted: 2021-06-29 11:23 PM
This was originally posted on APC forums on 11/28/2017
What would cause a Low Battery?
This is a new system and after restarting, it shows 25min of battery life.
I am also seeing several messages in the NMC log about distorted input and switching back and for to battery, like
11/14
6:40:13 UPS: on battery in response to distorted input
6:40:14 UPS: no longer on battery
11/19
7:57:55 UPS: on battery in response to distorted input
7:57:56 UPS: no longer on battery
8:03:23 UPS: on battery in response to distorted input
8:03:25 UPS: no longer on battery
20:13:53 UPS: on battery in response to distorted input
20:13:24 UPS: no longer on battery
PCNS has similar entries in its' log
Posted: 2021-06-29 11:23 PM
This reply was originally posted by Bill on APC forums on 11/30/2017
Hi,
The low battery setting on the NMC is at 15 minutes. When the UPS switched to battery and dropped below 15 minutes of runtime the shutdown was triggered. I cannot say why when restarted the UPS reports 25 minutes of runtime. It may have recharged or it may have only momentarily fallen below the threshold but the log shows it reported low battery so PCNS trigger the shutdown.
Posted: 2021-06-29 11:23 PM
This was originally posted on APC forums on 12/14/2017
The UPS was switched to battery for only 5 seconds when the source was moved from power strip to a wall oulet. How could the battery have dropped below 15 minutes?