Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79278members
343950posts

Outlet Sequence delay plus Shutdown Procedure delay, or not?

Solved
chrisbbb_apc
Ensign
Ensign
0 Likes
1
93

Outlet Sequence delay plus Shutdown Procedure delay, or not?

This was originally posted on APC forums on 9/25/2016


UPS SMX2200HV & PowerChute Business Edition 9.1.1 Build 604

Initial Settings - Shutdown Settings - Power Fail Config  - set to "begin shutdown procedure after the UPS as been on battery for" 300secs.

Outlet Sequence - "Time for other apps to shut down" 30secs plus "Time for os to shut down" 180secs, "Total time for outlet Group 1 to shutdown" 210secs.

My question: if the inlet mains power to UPS goes off, does Outlet Group 1 shut down 210secs later, or 510secs later?

Thanks

Chris


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
93

Re: Outlet Sequence delay plus Shutdown Procedure delay, or not?

This reply was originally posted by Bill on APC forums on 9/26/2016


Hi,

The UPS will run on battery for 300 seconds and then begin the shutdown process if AC is not restored. So, 300 second delay on battery, 30 second delay for application shutdown, then 180 second delay for OS shutdown. Total before outlet group powers off = 510 seconds. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
94

Re: Outlet Sequence delay plus Shutdown Procedure delay, or not?

This reply was originally posted by Bill on APC forums on 9/26/2016


Hi,

The UPS will run on battery for 300 seconds and then begin the shutdown process if AC is not restored. So, 300 second delay on battery, 30 second delay for application shutdown, then 180 second delay for OS shutdown. Total before outlet group powers off = 510 seconds.