Only one Smart UPS 3000 System recognized by PC - Connected through USB

Solved
Andrew.Posey_apc
Cadet
0 Likes
1
86

Only one Smart UPS 3000 System recognized by PC - Connected through USB

This was originally posted on APC forums on 5/24/2016


Hello,

I'm trying to set up monitoring for four Smart UPS 3000 systems on a single Windows 7 PC. When I connect all systems to the PC and run a search through USB, it only finds one system.

 

Is there any way to get all four connected through USB? Is it a simple setting I'm missing?

Thank you

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
86

Re: Only one Smart UPS 3000 System recognized by PC - Connected through USB

This reply was originally posted by Bill on APC forums on 5/25/2016


Hi,

You can only monitor 1 UPS at a time via USB. If you want to monitor 4 UPS from the same PC you should purchase network management cards for the Smart-UPS and then you can monitor the UPS via web interface, SSH, Telnet, or SNMP. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
87

Re: Only one Smart UPS 3000 System recognized by PC - Connected through USB

This reply was originally posted by Bill on APC forums on 5/25/2016


Hi,

You can only monitor 1 UPS at a time via USB. If you want to monitor 4 UPS from the same PC you should purchase network management cards for the Smart-UPS and then you can monitor the UPS via web interface, SSH, Telnet, or SNMP.