Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79537members
344364posts

Older AP9630 NMC2 card won't fit into Smart UPS 2200

Solved
rcoate_apc
Ensign
Ensign
0 Likes
4
228

Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 12/30/2015


What is the difference between the older AP9630 NMC2 cards with a shorter vertical slot/opening on the right-hand side of the card's front panel, and the newer AP9630 NMC2 cards with a taller slot?  Just replaced an older Smart UPS 2200 (SUA2200RM2U) with a newer Smart UPS 2200 (SMT2200RM2U), and mistakenly assumed that the old AP9630 NMC2 could be re-used.  It did not fit because there is a taller tab that requires the taller slot/opening to accommodate it. 

 

What is the difference - I thought any AP9630 NMC2 would be sufficient.

 

AP9630 NMC2

Attachments

Accepted Solutions
rcoate_apc
Ensign
Ensign
0 Likes
0
228

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 2/19/2016


As suggested, I called tech support and they happily sent me a replacement faceplate.

See Answer In Context

4 Replies 4
Terry_Kennedy_apc
Commander
Commander
0 Likes
0
228

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 12/30/2015


There was a run of those cards that incorrectly had the smaller tab. I forget the serial number range, but I think it was from 2009. I think if you call tech support with the card's serial number, they can send you a replacement faceplate. If not, post a reply and one of the APC folks here can probably get it to you.

BillP
Administrator Administrator
Administrator
0 Likes
0
228

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This reply was originally posted by Bill on APC forums on 1/4/2016


Robert,

Contact Technical Support at 1-800-890-4272 and they will send you out a replacement cover that has the proper size slots.

HarryAPC_apc
Cadet
0 Likes
0
228

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 2/19/2016


Yeah, I just had the same problem, faceplate with APC (not Schneider) and short slot on RHS.  PCB REV05 Copyright 2008.

I wanted to put the 9630 in an SMT1000, but it won't go.

So thanks for the info, I'll get the hacksaw out now....

Tags (3)
rcoate_apc
Ensign
Ensign
0 Likes
0
229

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 2/19/2016


As suggested, I called tech support and they happily sent me a replacement faceplate.