Older AP9630 NMC2 card won't fit into Smart UPS 2200

Solved
rcoate_apc
Ensign
Ensign
0 Likes
4
223

Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 12/30/2015


What is the difference between the older AP9630 NMC2 cards with a shorter vertical slot/opening on the right-hand side of the card's front panel, and the newer AP9630 NMC2 cards with a taller slot?  Just replaced an older Smart UPS 2200 (SUA2200RM2U) with a newer Smart UPS 2200 (SMT2200RM2U), and mistakenly assumed that the old AP9630 NMC2 could be re-used.  It did not fit because there is a taller tab that requires the taller slot/opening to accommodate it. 

 

What is the difference - I thought any AP9630 NMC2 would be sufficient.

 

AP9630 NMC2

Attachments

Accepted Solutions
rcoate_apc
Ensign
Ensign
0 Likes
0
223

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 2/19/2016


As suggested, I called tech support and they happily sent me a replacement faceplate.

See Answer In Context

4 Replies 4
Terry_Kennedy_apc
Commander
Commander
0 Likes
0
223

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 12/30/2015


There was a run of those cards that incorrectly had the smaller tab. I forget the serial number range, but I think it was from 2009. I think if you call tech support with the card's serial number, they can send you a replacement faceplate. If not, post a reply and one of the APC folks here can probably get it to you.

BillP
Administrator Administrator
Administrator
0 Likes
0
223

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This reply was originally posted by Bill on APC forums on 1/4/2016


Robert,

Contact Technical Support at 1-800-890-4272 and they will send you out a replacement cover that has the proper size slots.

HarryAPC_apc
Cadet
0 Likes
0
223

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 2/19/2016


Yeah, I just had the same problem, faceplate with APC (not Schneider) and short slot on RHS.  PCB REV05 Copyright 2008.

I wanted to put the 9630 in an SMT1000, but it won't go.

So thanks for the info, I'll get the hacksaw out now....

Tags (3)
rcoate_apc
Ensign
Ensign
0 Likes
0
224

Re: Older AP9630 NMC2 card won't fit into Smart UPS 2200

This was originally posted on APC forums on 2/19/2016


As suggested, I called tech support and they happily sent me a replacement faceplate.