Non-connected ap9617 cmos reset

Solved
bbailey_apc
Cadet
0 Likes
6
190

Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/3/2013


Is there anyway to reset the ap9617 to factory configuration without the ap9617 being in a UPS?  Removing the button battery does not clear the settings.

Thanks

Tags (1)

Accepted Solutions
Battman_apc
Commander
Commander
0 Likes
0
190

Re: Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/3/2013


I've done work on these cards with them installed in an AP9600 smartslot expansion chassis powered by a 24 vdc adapter...that's the only way to both power them and access them serially that I know of.

See Answer In Context

6 Replies 6
bbailey_apc
Cadet
0 Likes
0
190

Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/3/2013


Is there anyway to reset the ap9617 to factory configuration without the ap9617 being in a UPS?  Removing the button battery does not clear the settings.

Thanks

Battman_apc
Commander
Commander
0 Likes
0
191

Re: Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/3/2013


I've done work on these cards with them installed in an AP9600 smartslot expansion chassis powered by a 24 vdc adapter...that's the only way to both power them and access them serially that I know of.

Battman_apc
Commander
Commander
0 Likes
0
191

Re: Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/3/2013


...and what happens when the button battery dies ?   (something I've been meaning to find out for some time now !). ...Thanks!

bbailey_apc
Cadet
0 Likes
0
191

Re: Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/3/2013


Just a quick follow-up question.  What is the purpose of the button battery on the ap9617?

BillP
Administrator Administrator
Administrator
0 Likes
0
191

Re: Non-connected ap9617 cmos reset

This reply was originally posted by Angela on APC forums on 6/3/2013


It just keeps the date and time. I guess then if it fails just the date and time would reset when the card removed from power. I thought that for this type of application these would last upwards of 10 years potentially so then it might be time for an upgrade if it does die smile - it is not designed to be replaceable. On the newer cards it does not just 'pop out' but I think it might on the AP9617/18/19.

stevejenkins_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
191

Re: Non-connected ap9617 cmos reset

This was originally posted on APC forums on 6/30/2013


Arrgghhh.... Found this thread after searching and hoping that removing the battery from an AP9617 might reset the config. Time to go find my serial cable. smile