Posted: 2021-06-28 06:51 PM
This question was originally posted by Serge on APC forums on 10/20/2007
I beleive I'm having an issue with my SU5000TXFMR.
I'm only getting about 13min of Battery Life which by all calculations seems to be a fraction of what I should be getting.
My load power shows 26.5% Watts and the LED's on the unit for load show 2 lights. Looking at the runtime chart full load for my unit is 3375 watts so I figure I'm sitting at about 993 watts. Theirfor on the runtime chart I should be getting 51min.
The batteries were replaced today since the old ones have been in use since 2001. I figured my short runtime was due to the very old batteries. So I hot swapped in the new batteries Friday morning and let charge for about 8 hours and ran a runtime calibration. I got about 13min the same as the old batteries and it said they were discharged. I noticed that the Battery Voltage was about 46 volts when the UPS went back to mains and said the battery was discharged.
I let charge again for another 8 hours thinking maybe the unit needed to do a recharge cycle. I ran another calibration test and again around 13min it said the battery's were discharged. This time I noticed that the Battery Voltage was just over 49 volts when it went back to mains.
My question is what can I do to get the proper life out of my new batteries. Replacing the batteries on this unit is very expensive and I'm very concerned that I'm not getting the runtime that I should be getting. Since I hot swapped the batteries is there something I need to do to tell the UPS the batteries have changed? I figured a calibration would do that.
Thanks,
Serge.
Posted: 2021-06-28 06:51 PM
This reply was originally posted by Serge on APC forums on 10/20/2007
I beleive I'm having an issue with my SU5000TXFMR.
I'm only getting about 13min of Battery Life which by all calculations seems to be a fraction of what I should be getting.
My load power shows 26.5% Watts and the LED's on the unit for load show 2 lights. Looking at the runtime chart full load for my unit is 3375 watts so I figure I'm sitting at about 993 watts. Theirfor on the runtime chart I should be getting 51min.
The batteries were replaced today since the old ones have been in use since 2001. I figured my short runtime was due to the very old batteries. So I hot swapped in the new batteries Friday morning and let charge for about 8 hours and ran a runtime calibration. I got about 13min the same as the old batteries and it said they were discharged. I noticed that the Battery Voltage was about 46 volts when the UPS went back to mains and said the battery was discharged.
I let charge again for another 8 hours thinking maybe the unit needed to do a recharge cycle. I ran another calibration test and again around 13min it said the battery's were discharged. This time I noticed that the Battery Voltage was just over 49 volts when it went back to mains.
My question is what can I do to get the proper life out of my new batteries. Replacing the batteries on this unit is very expensive and I'm very concerned that I'm not getting the runtime that I should be getting. Since I hot swapped the batteries is there something I need to do to tell the UPS the batteries have changed? I figured a calibration would do that.
Thanks,
Serge.
Posted: 2021-06-28 06:51 PM
This was originally posted on APC forums on 10/22/2007
If the calibration key will work with your model, it will reset the runtime to new battery constant. It will only work if you are absolutely certain the new batteries meets the specs, otherwise you will get an over-estimate of runtime.
Posted: 2021-06-28 06:51 PM
This was originally posted on APC forums on 10/20/2007
Posted: 2021-06-28 06:51 PM
This reply was originally posted by Serge on APC forums on 10/20/2007
I beleive I'm having an issue with my SU5000TXFMR.
I'm only getting about 13min of Battery Life which by all calculations seems to be a fraction of what I should be getting.
My load power shows 26.5% Watts and the LED's on the unit for load show 2 lights. Looking at the runtime chart full load for my unit is 3375 watts so I figure I'm sitting at about 993 watts. Theirfor on the runtime chart I should be getting 51min.
The batteries were replaced today since the old ones have been in use since 2001. I figured my short runtime was due to the very old batteries. So I hot swapped in the new batteries Friday morning and let charge for about 8 hours and ran a runtime calibration. I got about 13min the same as the old batteries and it said they were discharged. I noticed that the Battery Voltage was about 46 volts when the UPS went back to mains and said the battery was discharged.
I let charge again for another 8 hours thinking maybe the unit needed to do a recharge cycle. I ran another calibration test and again around 13min it said the battery's were discharged. This time I noticed that the Battery Voltage was just over 49 volts when it went back to mains.
My question is what can I do to get the proper life out of my new batteries. Replacing the batteries on this unit is very expensive and I'm very concerned that I'm not getting the runtime that I should be getting. Since I hot swapped the batteries is there something I need to do to tell the UPS the batteries have changed? I figured a calibration would do that.
Thanks,
Serge.