Looking at interfacing to a Comet EX 7 RT UPS. Does anybody know which Network Management Cards can be used with this - I have found references on the web to SNMP Web Card 66074. Are any of the later NMC 2 cards compatible with this UPS ie. AP9630 or AP9635? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:10 AM . Last Modified: 2 weeks ago
Hi again - the MGE Comet is definitely not supported by any of the APC type of Network Management Cards (AP9630/31/35). So far, only some of the MGE Galaxy units have begun to be supported as per the link I sent you in your other thread (http://www.schneider-electric.us/en/faqs/FA237786). I only found reference to MGE NMC 66074 for the Comet as you did.
Furthermore, the firmware you put on the MGE NMC 66074 may matter for the Comet UPS which the 3 phase technical support team would supply for you after checking a few items.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:10 AM . Last Modified: 2 weeks ago
Hi again - the MGE Comet is definitely not supported by any of the APC type of Network Management Cards (AP9630/31/35). So far, only some of the MGE Galaxy units have begun to be supported as per the link I sent you in your other thread (http://www.schneider-electric.us/en/faqs/FA237786). I only found reference to MGE NMC 66074 for the Comet as you did.
Furthermore, the firmware you put on the MGE NMC 66074 may matter for the Comet UPS which the 3 phase technical support team would supply for you after checking a few items.