Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79539members
344372posts

NMC2 ping Gateway by itself

Solved
ITgustl_apc
Cadet
0 Likes
2
198

NMC2 ping Gateway by itself

This was originally posted on APC forums on 9/25/2020


Hi,

two of our NMC2 ping our Gateway by itself, please see the picture attached.
10.10.1.212 and 10.10.1.213 are NMC2
10.10.0.1 is the Gateway

Question: What setting in the NMC2 triggers these automated pings? All other NMC2 do this not.

Thanks

Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
198

Re: NMC2 ping Gateway by itself

This reply was originally posted by Gavan on APC forums on 9/28/2020


Hi Marc,

Any new cards that come from the factory with Fw6.8.x or newer won't do this as SNMP is disabled by default, you can also disable it via the WebGUI.

-Gavan

See Answer In Context

2 Replies 2
ITgustl_apc
Cadet
0 Likes
0
198

Re: NMC2 ping Gateway by itself

This was originally posted on APC forums on 9/25/2020


Hi, found the answer myself after comparing the Config-Files from affected and unaffected NMC2s.
The only difference (beside the MAC, IP, Names...) are the TrapReceiver5Community=public and TrapReceiver6Community=public entries.

The affected (generating automated pings to the gateway) NMC2 have the following conf lines in the [NetworkSNMP] block:

TrapReceiver5Community=public
TrapReceiver6Community=public

Unaffected NMC2 have this entry in the [NetworkSNMP] block:

TrapReceiver5Community=""
TrapReceiver6Community=""

I copied the whole [NetworkSNMP] block from an unaffected NMC2 to a new config-file (ini) and imported this file (with only the [NetworkSNMP] block) in the affected NMC2. After this and rebooting the NMC2, no pings are generated anymore.

Regards

BillP
Administrator Administrator
Administrator
0 Likes
0
199

Re: NMC2 ping Gateway by itself

This reply was originally posted by Gavan on APC forums on 9/28/2020


Hi Marc,

Any new cards that come from the factory with Fw6.8.x or newer won't do this as SNMP is disabled by default, you can also disable it via the WebGUI.

-Gavan