Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-07-08 12:37 AM
This was originally posted on APC forums on 5/18/2015
Hello Community,
The .EXE upgrade procces failed during NMC restart after 1/3 (boot monitor transfering) upgrade phase (the UPS itself restarted -> the connected server lost power for a short moment) (see screenshot):
Now I'm getting "Application Error" if I'm trying to open Web-Console(see screenshot):
After EXE-Upgrade I also tried to upgrade via FTP, but it didn't work too, it stops coping firmware at one point:
I can't download a debug too...
Here is teh satus message if I conenct to the CLI console:
Stat : P+ N4+ N6+ A-
Do you think the NetworkCard is damaged? and need to be replaced? or do you have any ideas?
Thank you!
Posted: 2021-07-08 12:38 AM
This reply was originally posted by Angela on APC forums on 5/18/2015
Hi,
I think what you have a problem with potentially is your FTP data port being blocked. FTP uses two ports, 20 and 21. I have seen this when you can log in via FTP but cannot transfer data though. I don't know why it would've worked through the utility though..
The AP9631 definitely will not have to be replaced and we'll get this working. We need to do one or more of the following things though:
Let me know if you have any questions before you get started.
Posted: 2021-07-08 12:38 AM
This reply was originally posted by Angela on APC forums on 5/18/2015
Hi,
I think what you have a problem with potentially is your FTP data port being blocked. FTP uses two ports, 20 and 21. I have seen this when you can log in via FTP but cannot transfer data though. I don't know why it would've worked through the utility though..
The AP9631 definitely will not have to be replaced and we'll get this working. We need to do one or more of the following things though:
Let me know if you have any questions before you get started.
Posted: 2021-07-08 12:38 AM
This was originally posted on APC forums on 5/18/2015
Hi Angela,
You were right! That was an issue with the windows Firewall.
Thank you!
User | Count |
---|---|
4834 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.