NMC Upgrade failed - can't access web interface anymore - Smart-UPS X 2000 - AP9631

This was originally posted on APC forums on 5/18/2015


Hello Community,

The .EXE upgrade procces failed during NMC restart after 1/3 (boot monitor transfering) upgrade phase (the UPS itself restarted -> the connected server lost power for a short moment) (see screenshot):

Now I'm getting "Application Error" if I'm trying to open Web-Console(see screenshot):

After EXE-Upgrade I also tried to upgrade via FTP, but it didn't work too, it stops coping firmware at one point:

I can't download a debug too...

Here is teh satus message if I conenct to the CLI console:

Stat : P+ N4+ N6+ A-

Do you think the NetworkCard is damaged? and need to be replaced? or do you have any ideas?

Thank you!

Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
705

Re: NMC Upgrade failed - can't access web interface anymore - Smart-UPS X 2000 - AP9631

This reply was originally posted by Angela on APC forums on 5/18/2015


Hi,

I think what you have a problem with potentially is your FTP data port being blocked. FTP uses two ports, 20 and 21. I have seen this when you can log in via FTP but cannot transfer data though. I don't know why it would've worked through the utility though..

The AP9631 definitely will not have to be replaced and we'll get this working. We need to do one or more of the following things though:

  • Address what is wrong with the FTP protocol's data port - maybe try a different computer, temporarily disable any firewall or other services that could be blocking it, etc. I had this on my own work PC once and it was the Cisco VPN service/stateful packet inspection doing it (when I wasn't connected to VPN!)

Let me know if you have any questions before you get started.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
706

Re: NMC Upgrade failed - can't access web interface anymore - Smart-UPS X 2000 - AP9631

This reply was originally posted by Angela on APC forums on 5/18/2015


Hi,

I think what you have a problem with potentially is your FTP data port being blocked. FTP uses two ports, 20 and 21. I have seen this when you can log in via FTP but cannot transfer data though. I don't know why it would've worked through the utility though..

The AP9631 definitely will not have to be replaced and we'll get this working. We need to do one or more of the following things though:

  • Address what is wrong with the FTP protocol's data port - maybe try a different computer, temporarily disable any firewall or other services that could be blocking it, etc. I had this on my own work PC once and it was the Cisco VPN service/stateful packet inspection doing it (when I wasn't connected to VPN!)

Let me know if you have any questions before you get started.

apc15kva_apc
Ensign
Ensign
0 Likes
0
705

Re: NMC Upgrade failed - can't access web interface anymore - Smart-UPS X 2000 - AP9631

This was originally posted on APC forums on 5/18/2015


Hi Angela,

You were right! That was an issue with the windows Firewall.

Thank you!