I have a server room with 11 servers, 3 24-drive SAS RAID arrays, 2 SAS tape drives, and an assortment of small bits like switches, a small NAS box, a monitor, etc, all powered from 10 Smart-UPS 1500s--8 of the older LED type, and 2 of the newer LCD type. The servers run ESXi Hypervisor (3), Linux (2), and Windows Server 2008 (6). I'd like a solution that will let me do the following:
- Monitor all 10 UPSs with PowerChute.
- If there is a power failure and the generator fails to come online (or runs out of fuel), perform a proper shut down of the servers when the UPSs are running low.
- If at all possible, not have to buy any SmartSlot network management cards.
The servers are _not_ one-to-one server-to-UPS. The servers all have two power supplies, so those are split between two UPSs for redundancy--also, I have more servers than UPSs, and this will stay the same, as my UPSs run below 50% capacity, letting me add more servers without buying more UPSs. I was wondering it it's possible to use any version of PowerChute to do the following:
- Have 10 UPSs connected to one server with a large UPS hub, and install PowerChute on that server.
- During a power failure, when any one of the UPSs has 3 minutes left, issue a shutdown to _all_ the servers.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2 weeks ago
Unfortunately, I don't see a viable way to do do this without utilizing UPS Network Management Cards in some type of Redundant/multiple UPS setup Scenario. The only other option is to use a Share UPS with a bunch of serial cables all over the place directly connected between UPS/server and you cannot do that with servers with redundant power supplies. Only PowerChute Network Shutdown with a UPS Network Management Card can support a redundant/multiple UPS Scenario that I think you are looking for.
The PowerChute Network Shutdown help file has some good information and so does this document ->http://www.apcmedia.com/salestools/BKIR-6R9NX5/BKIR-6R9NX5_R2_EN.pdf
Just my two cents though.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 2 weeks ago
Unfortunately, I don't see a viable way to do do this without utilizing UPS Network Management Cards in some type of Redundant/multiple UPS setup Scenario. The only other option is to use a Share UPS with a bunch of serial cables all over the place directly connected between UPS/server and you cannot do that with servers with redundant power supplies. Only PowerChute Network Shutdown with a UPS Network Management Card can support a redundant/multiple UPS Scenario that I think you are looking for.
The PowerChute Network Shutdown help file has some good information and so does this document ->http://www.apcmedia.com/salestools/BKIR-6R9NX5/BKIR-6R9NX5_R2_EN.pdf
Just my two cents though.