Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-07-08 12:41 AM
This question was originally posted by Nestor on APC forums on 6/1/2015
Hi, excuse me i need some information about the description of the columns of this data. For example, Vmin its rms?. And how can i use this logs for discover electrical problems. Thanks for you help.
Posted: 2021-07-08 12:41 AM
This reply was originally posted by Nestor on APC forums on 6/1/2015
Thanks for you answer, its for use the log capabilities use logs saved for a week or a month.
What is the minium time of data log save a valor? a minute? Thanks for you answer.
Posted: 2021-07-08 12:41 AM
This was originally posted on APC forums on 6/1/2015
Yes, AC voltages are in RMS.
As for discovering electrical problems, to set your expectations: the UPS isn't a power line diagnostic tool so capabilities are limited. The log will show if the voltage is high or low or the frequency out of range over an extended period of time. Electrical issues over a short timespan may not show up in the data log*, but may cause the UPS to transfer to battery which will show up in the event log. Issues with grounding, missing neutral, neutral and hot swapped, etc may show up as "site wiring fault".
* You'd think they'd show up in Vmin and Vmax but unfortunately brief events do not necessarily show up here.
Posted: 2021-07-08 12:41 AM
This reply was originally posted by Nestor on APC forums on 6/1/2015
Thanks for you answer, its for use the log capabilities use logs saved for a week or a month.
What is the minium time of data log save a valor? a minute? Thanks for you answer.
User | Count |
---|---|
4834 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.