Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79278members
343949posts

Monitoring and how use logs.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
2
139

Monitoring and how use logs.

This question was originally posted by Nestor on APC forums on 6/1/2015


Hi, excuse me i need some information about the description of the columns of this data. For example, Vmin its rms?. And how can i use this logs for discover electrical problems. Thanks for you help.

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
139

Re: Monitoring and how use logs.

This reply was originally posted by Nestor on APC forums on 6/1/2015


Thanks for you answer, its for use the log capabilities use logs saved for a week or a month.

What is the minium time of data log save a valor? a minute? Thanks for you answer.

See Answer In Context

2 Replies 2
voidstar_apc
Janeway
Janeway
0 Likes
0
139

Re: Monitoring and how use logs.

This was originally posted on APC forums on 6/1/2015


Yes, AC voltages are in RMS.

As for discovering electrical problems, to set your expectations: the UPS isn't a power line diagnostic tool so capabilities are limited. The log will show if the voltage is high or low or the frequency out of range over an extended period of time. Electrical issues over a short timespan may not show up in the data log*, but may cause the UPS to transfer to battery which will show up in the event log. Issues with grounding, missing neutral, neutral and hot swapped, etc may show up as "site wiring fault".

* You'd think they'd show up in Vmin and Vmax but unfortunately brief events do not necessarily show up here.

BillP
Administrator Administrator
Administrator
0 Likes
0
140

Re: Monitoring and how use logs.

This reply was originally posted by Nestor on APC forums on 6/1/2015


Thanks for you answer, its for use the log capabilities use logs saved for a week or a month.

What is the minium time of data log save a valor? a minute? Thanks for you answer.