Hello...
I have Matrix UPS 3000 connected to spectrometer and computer. The computer freeze up quite often for the last 2 weeks for which reason I am not sure. Here is what I have done.
1) I did UPS TEST > Battery Cal TEST> DO and the message showed "Not possible at this time..." what is that mean? I couldn't find this error message in user's manual.
2) I unplug the spectrometer from the wall and run on battery and it works fine, all the communication can run on UPS batteries. I am not sure why the computer froze every 2-3 times a week. Also, I don't know much about electronics so please explain in a layman's term. Thank you for your help.
Hla
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:12 AM . Last Modified: 2024-03-12 03:13 AM
Hello,
I don't think it is likely the UPS is causing this problem with the computer.
A battery calibration only calibrates the reported runtime that the UPS has. Why it would not perform a calibration is outlined here -> - Matrix UPS will not perform a runtime calibration | FAQs | Schneider Electric US Maybe you meant to run a self test or just battery test?
The isolation transformer in the Matrix would practically guarantees clean power to the attached devices. The only thing I am familiar with electronics having a problem or freezing is because of grounding issues which would have nothing to do with the UPS.
You may want to look specifically at the computer - is it older, is it something perhaps with the operating system on it rather than the power input, etc?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:12 AM . Last Modified: 2024-03-12 03:13 AM
Hello,
I don't think it is likely the UPS is causing this problem with the computer.
A battery calibration only calibrates the reported runtime that the UPS has. Why it would not perform a calibration is outlined here -> - Matrix UPS will not perform a runtime calibration | FAQs | Schneider Electric US Maybe you meant to run a self test or just battery test?
The isolation transformer in the Matrix would practically guarantees clean power to the attached devices. The only thing I am familiar with electronics having a problem or freezing is because of grounding issues which would have nothing to do with the UPS.
You may want to look specifically at the computer - is it older, is it something perhaps with the operating system on it rather than the power input, etc?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.