Mac OS X Server 10.7 computer doesn't display UPS options in Energy Saver
Mac specs: Mac Pro, 2.8ghz quad core intel, 12gb ram, OS X Server 10.7.5
UPS specs: APC Smart-UPS SC1000 2U Rackmount Tower
Purchase date: Jan 2012
USB Cable: APC USB to Serial Smart Signaling Cable Model AP9833
#1 Using the System Information App USB section I can see that the Mac recognizes the cable as a USB-Serial Controller "Prolific Technology"
#2 The energy saver control panel does not display any UPS info and the System Information App Power section does not display any UPS info.
#3 We have tried unplugging the cable.
#4 We have tried installing apcupsd (which we use on our all linux boxes) - but it can not detect the UPS
Suggestions?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
did you ever get a driver for that prolific device? i've never used it on a Mac but I know on Windows it requires a driver to be installed. is the Mac indicating it is installed properly or did it just detect it and we might need a driver? i asked someone about this and they seemed to indicate that it is the same case on the Mac - driver needed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
um - no. no success.
tried installing the prolific drivers - and rebooted - no luck.
shutdown the mac and power cycled the UPS - no luck.
I tried this on two different Macs running different OS X versions.
gave up - ordered UPS from another vendor.
I still like APC just not Mac compatible for me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
Sorry
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
the AP9833 is only a USB to serial adapter. you will still need the UPS communication cable that came with your UPS.
i believe your SC1000 came with a serial cable, part number 940-0024 or 940-1524, correct? it has a serial connector on both ends.
i think what you should have here is SC1000->940-0024/940-1524 serial cable->DB-9 end of AP9833->AP9833 USB end to your server.
can you try it this way and share results?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
we tried this without success
we daisy chained the two cables together but no luck
i rebooted the mac no luck
the mac detects the usb cable but that's all
anything else to try or is it time to move to a new ups?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
looks good!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:07 AM . Last Modified: 2024-03-05 11:54 PM
did you ever get a driver for that prolific device? i've never used it on a Mac but I know on Windows it requires a driver to be installed. is the Mac indicating it is installed properly or did it just detect it and we might need a driver? i asked someone about this and they seemed to indicate that it is the same case on the Mac - driver needed.