Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80586members
346494posts

Lost Communication to the UPS after firmware update

Solved
NikSpasov
Crewman
Crewman
0 Likes
3
370

Lost Communication to the UPS after firmware update

Hello,

I have APC Smart-UPS 2200VA LCD 230V (SMT2200I) with AP9631 and before the firmware update, everything was fine.

After the update, I have "Lost Communication to the UPS".

 

 

Could you help me, please?

Thanks,
Nik

 

Screenshot 2022-01-17 185229.jpg

Tags (1)

Accepted Solutions
Shaun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
367

Re: Lost Communication to the UPS after firmware update

Hi @NikSpasov,

 

Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.

 

The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...

 

As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.

 

Regards,

  Shaun

See Answer In Context

Tags (1)
3 Replies 3
Shaun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
368

Re: Lost Communication to the UPS after firmware update

Hi @NikSpasov,

 

Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.

 

The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...

 

As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.

 

Regards,

  Shaun

Tags (1)
NikSpasov
Crewman
Crewman
0 Likes
1
361

Re: Lost Communication to the UPS after firmware update

Thank you very much, @Shaun,

Somehow, I successfully killed the network card.

 

I have downloaded this: file apc_hw05_aos704_sumx704_bootmon109.exe
In the middle of installation, the tool lost connection to UPS. (FTP method)

Now I can't find the network card anymore.

 

Do you have any idea how to fix this mess?

 

Thanks

Nik

 

Tags (2)
NikSpasov
Crewman
Crewman
0 Likes
0
346

Re: Lost Communication to the UPS after firmware update

Hi @Shaun ,

Everything is fine now. 

The new firmware has disabled HTTP communication. HTTPS is enabled and now all works fine.

Thank you very much!

All the best,

Nik

Tags (1)