Lost Communication to the UPS after firmware update

Solved
NikSpasov
Crewman
Crewman
0 Likes
3
400

Lost Communication to the UPS after firmware update

Hello,

I have APC Smart-UPS 2200VA LCD 230V (SMT2200I) with AP9631 and before the firmware update, everything was fine.

After the update, I have "Lost Communication to the UPS".

 

 

Could you help me, please?

Thanks,
Nik

 

Screenshot 2022-01-17 185229.jpg

Tags (1)

Accepted Solutions
Shaun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
397

Re: Lost Communication to the UPS after firmware update

Hi @NikSpasov,

 

Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.

 

The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...

 

As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.

 

Regards,

  Shaun

See Answer In Context

Tags (1)
3 Replies 3
Shaun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
398

Re: Lost Communication to the UPS after firmware update

Hi @NikSpasov,

 

Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.

 

The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...

 

As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.

 

Regards,

  Shaun

Tags (1)
NikSpasov
Crewman
Crewman
0 Likes
1
391

Re: Lost Communication to the UPS after firmware update

Thank you very much, @Shaun,

Somehow, I successfully killed the network card.

 

I have downloaded this: file apc_hw05_aos704_sumx704_bootmon109.exe
In the middle of installation, the tool lost connection to UPS. (FTP method)

Now I can't find the network card anymore.

 

Do you have any idea how to fix this mess?

 

Thanks

Nik

 

Tags (2)
NikSpasov
Crewman
Crewman
0 Likes
0
376

Re: Lost Communication to the UPS after firmware update

Hi @Shaun ,

Everything is fine now. 

The new firmware has disabled HTTP communication. HTTPS is enabled and now all works fine.

Thank you very much!

All the best,

Nik