Good afternoon! Often there are problems in the APC program PowerShute loses contact with the UPS. In the device manager, the UPS is visible installed. The cables were replaced. The problem is fixed for a while and then reappears. How can I solve the problem? Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 AM . Last Modified: 2024-03-15 05:42 AM
Hi,
What is recorded in the event log? Is PowerChute recording enabling Green Mode and then comm is lost? If so, disable Green Mode, restart the PowerChute service and that should resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:18 AM . Last Modified: 2024-03-15 05:42 AM
Hi,
What is recorded in the event log? Is PowerChute recording enabling Green Mode and then comm is lost? If so, disable Green Mode, restart the PowerChute service and that should resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.