Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80811members
346877posts

Is PowerChute BE compatible with BMI card(AP9622)?

Solved
yopark_apc
Ensign
Ensign
0 Likes
2
177

Is PowerChute BE compatible with BMI card(AP9622)?

This was originally posted on APC forums on 3/2/2010


Hi all,

I am just wondering if Powerchute BE can communicate with BMI card(AP9622) installed in the silcon 480kw.
I just wanted to know how to monitor issues from silcon 480kw by using BMI card(AP9622).
There is only one BMI card installed in the Triple chassis(AP9604S) and it communicates with Building Management Systems.
However, BMS somtimes shows wired issues which is not understandable. For example, it represents a huge amount of different issues generated at the same time. so, I just came down to silcon to check if these issues are correct, but any closed issues were not shown.

I think this issues might come from silcon ups or triple chassis. Therefore, I decided to monitor silcon ups in different way jus like mentioned above.

Is there any other way to monitor silcon ups's logs???

Thank you for reading this.


Accepted Solutions
yopark_apc
Ensign
Ensign
0 Likes
0
177

Re: Is PowerChute BE compatible with BMI card(AP9622)?

This was originally posted on APC forums on 3/3/2010


Thanks for your help!! ^^

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
177

Re: Is PowerChute BE compatible with BMI card(AP9622)?

This reply was originally posted by Angela on APC forums on 3/2/2010


powerchute business edition cannot read data from the AP9622 unfortunately. you can only use a BMS to read data from the card.

PCBE can only see data from other accessories such as the AP9612TH.

yopark_apc
Ensign
Ensign
0 Likes
0
178

Re: Is PowerChute BE compatible with BMI card(AP9622)?

This was originally posted on APC forums on 3/3/2010


Thanks for your help!! ^^