Hi all
Please let me know what happens if I put the Input Phase Selector Switch not in accordance with the power feeding:
- Connect the UPS to a three phase mains and put the switch in "1"
- Connect the UPS in single phase and put the switch in "3"
Can the UPS become damaged because of this mismatch?
Please consider SURT10000XLI UPS.
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:13 AM . Last Modified: 2024-03-10 11:57 PM
Hi,
I dont have any experience with this issue.
1. But as my knowleage, the switch selection in "1 "will make a solid connect between 3phase input. You will got the short - circuit in case apply the 3 phase to this selection.
Why ?
Rectifier only provide convert from AC to DC.
The IGBT (or SCR in each phase is sized ~ 10kVA/3). in 3:1 mode, it's ok
In the 1:1 mode, the L1 can't support enough capacity so it's will make a solid 3 phase. L1, L2, L3. (The bypass only take from L1).
2. If you put the single phase to but select 3 phase. It's won't have any issue (this is site wiring failure alarm, or make the Input outside of tolerat - run battery).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:12 AM . Last Modified: 2024-03-10 11:58 PM
Hi
Thanks for your post but you are wrong.
Your speech assumes that the "input selector phase switch" is a power one and it is not. It is a signal switch, and acts to the control like a setup parameter. It has influence on the UPS behavior and, I think, on the way control modulates input switching when supplying the internal inverter from AC mains.
The UPS doesn't have a controlled switch - IGBT module - per phase. Instead it has a bridge rectifier per phase (two bridges in parallel on phase L1 to support 1:1 running). IGBT modules are assembled after input rectification.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:12 AM . Last Modified: 2024-03-10 11:58 PM
Definitely no one knows something about this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:12 AM . Last Modified: 2024-03-10 11:58 PM
Hi all
Are you in vacations
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:12 AM . Last Modified: 2024-03-10 11:57 PM
Hi there
Pleeeeeeease can you leave here any support to my inquiry?
I have one SURT10000XLI that was connected to a three phase system with the phase selector switch in the position "1".
The input/battery converter - PFC or DC/DC from batteries - became damaged. One IGBT module was broken.
I would like to know if those things - switch position and converter damage - can be correlated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:13 AM . Last Modified: 2024-03-10 11:57 PM
Hi,
I dont have any experience with this issue.
1. But as my knowleage, the switch selection in "1 "will make a solid connect between 3phase input. You will got the short - circuit in case apply the 3 phase to this selection.
Why ?
Rectifier only provide convert from AC to DC.
The IGBT (or SCR in each phase is sized ~ 10kVA/3). in 3:1 mode, it's ok
In the 1:1 mode, the L1 can't support enough capacity so it's will make a solid 3 phase. L1, L2, L3. (The bypass only take from L1).
2. If you put the single phase to but select 3 phase. It's won't have any issue (this is site wiring failure alarm, or make the Input outside of tolerat - run battery).
Link copied. Please paste this link to share this article on your social media post.