Most of the systems I've seen for Row based cooling having the compressor in the row unit and then outside condenser. I've seen some other manufacturers that instead have a condensing unit and then the row based unit doesn't contain the compressor and has more fans for a higher kW cooling capacity ... Does APC have any in row unit thats use an outside condensing unit vs condenser?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:40 PM . Last Modified: 1 week ago
Hello Joshua. All of our air cooled (DX) units have the compressor inside the indoor unit. We do not have any units with the compressor in the condenser. The closest thing we would have to this is the chilled water units, that require a chiller unit outside that contains the compressor.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:40 PM . Last Modified: 1 week ago
Hello Joshua. All of our air cooled (DX) units have the compressor inside the indoor unit. We do not have any units with the compressor in the condenser. The closest thing we would have to this is the chilled water units, that require a chiller unit outside that contains the compressor.