Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-28 07:04 AM
This question was originally posted by John on APC forums on 8/20/2013
In setting up an InRow, I discovered that you need to connect an Ethernet cable to the comms card for network capability AND you need to connect all the devices together using the A-link connections so the units will communicate as a group. That is a lot of cable. Can I only connect them using the Comms connection to my network and then tell them which units are in the same group?
Please advise if I can or if not, why? does it have to do with not flooding the network lines with data packets between the units?
Regards,
J
Posted: 2021-06-28 07:04 AM
This reply was originally posted by L2SupportServices-Cooling on APC forums on 8/20/2013
Sure thing!
J.Smith:
In regards to the various connections on the unit, unfortunately group communication cannot be done via the ethernet connection. This connection is only for communication to the web interface of the device, as well as other forms of network communication such as email or SNMP. The group communication is done via A-link ports, and while they use ethernet connections to make the cabling standard, it is effectively a serial bus, and shares nothing with normal network communication, hence why it is done this way. I apologize for any inconvenience, but if you have any other questions, please feel free to ask. Thank you.
Posted: 2021-06-28 07:04 AM
This reply was originally posted by Angela on APC forums on 8/20/2013
L2SupportServices-Cooling - could you help with this one please? Thanks!
Posted: 2021-06-28 07:04 AM
This reply was originally posted by L2SupportServices-Cooling on APC forums on 8/20/2013
Sure thing!
J.Smith:
In regards to the various connections on the unit, unfortunately group communication cannot be done via the ethernet connection. This connection is only for communication to the web interface of the device, as well as other forms of network communication such as email or SNMP. The group communication is done via A-link ports, and while they use ethernet connections to make the cabling standard, it is effectively a serial bus, and shares nothing with normal network communication, hence why it is done this way. I apologize for any inconvenience, but if you have any other questions, please feel free to ask. Thank you.
User | Count |
---|---|
4836 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.