IBM eSERVER UPS 1500THV

Solved
ausafali88_apc
Cadet
0 Likes
1
102

IBM eSERVER UPS 1500THV

This was originally posted on APC forums on 6/1/2016


Dear Members;

Sorry for a stupid question.....embarassed

I have heard that IBM eSERVER UPS's series was acquired by APC....The issue i am facing now is that i have an IBM UPS 1500 THV eSERVER...and when i connect a serial cable to manage it from a PowerChute Server it shuts off...This is due to a non-standard serial cable being used....

Pls  can anyone suggest what serial cable should i use...should i contact IBM now...or will APC serial cables do the job....

Waiting eagerly for your kind repliesfoot-in-mouth

Regards.

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
103

Re: IBM eSERVER UPS 1500THV

This reply was originally posted by Bill on APC forums on 6/2/2016


Hi,

We did not acquire the IBM eServer UPS line. We are the OEM. 

The cable you need is part number 940-0024 and can be purchase at CDW, Amazon, New Egg, APC.com, and many other on-line retailers. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
104

Re: IBM eSERVER UPS 1500THV

This reply was originally posted by Bill on APC forums on 6/2/2016


Hi,

We did not acquire the IBM eServer UPS line. We are the OEM. 

The cable you need is part number 940-0024 and can be purchase at CDW, Amazon, New Egg, APC.com, and many other on-line retailers.