Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79292members
343972posts

IBM eSERVER UPS 1500THV

Solved
ausafali88_apc
Cadet
0 Likes
1
100

IBM eSERVER UPS 1500THV

This was originally posted on APC forums on 6/1/2016


Dear Members;

Sorry for a stupid question.....embarassed

I have heard that IBM eSERVER UPS's series was acquired by APC....The issue i am facing now is that i have an IBM UPS 1500 THV eSERVER...and when i connect a serial cable to manage it from a PowerChute Server it shuts off...This is due to a non-standard serial cable being used....

Pls  can anyone suggest what serial cable should i use...should i contact IBM now...or will APC serial cables do the job....

Waiting eagerly for your kind repliesfoot-in-mouth

Regards.

Tags (4)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
100

Re: IBM eSERVER UPS 1500THV

This reply was originally posted by Bill on APC forums on 6/2/2016


Hi,

We did not acquire the IBM eServer UPS line. We are the OEM. 

The cable you need is part number 940-0024 and can be purchase at CDW, Amazon, New Egg, APC.com, and many other on-line retailers. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
101

Re: IBM eSERVER UPS 1500THV

This reply was originally posted by Bill on APC forums on 6/2/2016


Hi,

We did not acquire the IBM eServer UPS line. We are the OEM. 

The cable you need is part number 940-0024 and can be purchase at CDW, Amazon, New Egg, APC.com, and many other on-line retailers.