Posted: 2021-06-28 03:32 AM
This was originally posted on APC forums on 3/12/2016
NMC 2 not communicating with UPS. Model#SMX3000LVNC. How can I fix this. I have been beating my head for days on this.
Posted: 2021-06-28 03:32 AM
This reply was originally posted by Bill on APC forums on 3/13/2016
Hi,
The NMC has the wrong firmware installed and that is why it will not discover the SMX3000. You need to install SUMX6.4 from this link
Posted: 2021-06-28 03:32 AM
This reply was originally posted by Bill on APC forums on 3/13/2016
Hi,
The NMC has the wrong firmware installed and that is why it will not discover the SMX3000. You need to install SUMX6.4 from this link
Posted: 2021-06-28 03:32 AM
This was originally posted on APC forums on 3/13/2016
Thank you very much!