Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80959members
347132posts

I can't login to the PCNS v3 Webinterface...

Solved
flowww_apc
Crewman
Crewman
0 Likes
5
310

I can't login to the PCNS v3 Webinterface...

This was originally posted on APC forums on 1/31/2012


Hi there,

I hope you can help me with this one...

I can't login to the PowerChute Network Shutdown Webinterface.

I installed PCNS v3 for the fist time on a server and after finishing the first-time-configuration-wizzard I'm in the webinterface and everything looks good.

After a few hours I want to access the Webinterface again but...

https://servername:6547
"Log on to PowerChute to monitor and configure shutdown"
*"Invalid User name or Password. Please try again"*

I already tried all the Login & Passwords I could think of.

Please help, Florian

Tags (1)

Accepted Solutions
teddybearbeer_apc
Crewman
Crewman
0 Likes
0
310

Re: I can't login to the PCNS v3 Webinterface...

This was originally posted on APC forums on 3/19/2018


I just stopped process pcns.exe and started again...

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
310

Re: I can't login to the PCNS v3 Webinterface...

This reply was originally posted by Angela on APC forums on 1/31/2012


this would have been whatever you entered when it was installed. generally the administrator username is the same as what it is on your network management card. also, you can try pressing the logon button, versus pressing enter on the page to see if that helps.

if you don't know your password, on PCNS v3, you can reset the password. this article also might be applicable: http://nam-en.apc.com/app/answers/detail/a_id/11382/

flowww_apc
Crewman
Crewman
0 Likes
0
310

Re: I can't login to the PCNS v3 Webinterface...

This was originally posted on APC forums on 1/31/2012


Thanks for your answer!

Yes, I had a special character in the NMC password... 😞

I changed the NMC password and I also changed the password of the PCNS according to http://nam-en.apc.com/app/answers/detail/a_id/11382/
but unfortunately I'm still not able to login.

Any other ideas?

Thanks in advanced,
Florian

flowww_apc
Crewman
Crewman
0 Likes
0
310

Re: I can't login to the PCNS v3 Webinterface...

This was originally posted on APC forums on 1/31/2012


OK, I got it!

Eventhough the username was correct - I had to change it too in the INI-File.

Now it's working...

Many thanks.

BillP
Administrator Administrator
Administrator
0 Likes
0
310

Re: I can't login to the PCNS v3 Webinterface...

This reply was originally posted by Angela on APC forums on 1/31/2012


no problem!

teddybearbeer_apc
Crewman
Crewman
0 Likes
0
311

Re: I can't login to the PCNS v3 Webinterface...

This was originally posted on APC forums on 3/19/2018


I just stopped process pcns.exe and started again...