Hi everybody,
I have an UPS network management card with information as below:
Model Number: | AP9619 |
Serial Number: | BA0936001269 |
I am developing a tool monitor my UPS.
so my problem is: how can I get the current temperature of the UPS by commandline on Windows OS.
please help me....
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:05 AM . Last Modified: 1 month ago
You can get those values (and many others) via SNMP. There are a large number of SNMP tools available for Windows. I use Net-SNMP, although not on Windows. Depending on your UPS model, there may be several temperature values available (UPS internal temperature, battery temperature, etc.). And since you have an AP9619, you may also have an external temperature (and perhaps humidity) probe.
If you need the OIDs, post a reply and I'll look them up.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:05 AM . Last Modified: 1 month ago
You can get those values (and many others) via SNMP. There are a large number of SNMP tools available for Windows. I use Net-SNMP, although not on Windows. Depending on your UPS model, there may be several temperature values available (UPS internal temperature, battery temperature, etc.). And since you have an AP9619, you may also have an external temperature (and perhaps humidity) probe.
If you need the OIDs, post a reply and I'll look them up.