Posted: 2021-06-30 06:02 AM
This was originally posted on APC forums on 9/24/2020
Hi, I don't have much experience with APC products or UPS in general but I'm looking for an easy way to remotely figure out which management card is installed in a Galaxy 5000 60 KVA.
I have access to Struxtureware Data center Expert but I still can't figure which model it is.
Looking to download the corresponding PowerNet Mib file once I have the model number.
any help would be appreciated!
Posted: 2021-06-30 06:02 AM
This reply was originally posted by Gavan on APC forums on 9/29/2020
I believe you have a pre-APC card, the MGE SNMP Web Card - 66074 (KD revision)
https://www.se.com/ww/en/product/66074/mge-snmp-web-card/
The below FAQ has a video that you can use to confimr:
https://www.se.com/ww/en/faqs/FA281356/
-Gavan
Posted: 2021-06-30 06:02 AM
This reply was originally posted by Bill on APC forums on 9/28/2020
Hi,
It will depend on the card and firmware. Log in to the card and go to About - Network. You will see the model and firmware info.
Posted: 2021-06-30 06:02 AM
This was originally posted on APC forums on 9/28/2020
I don't see "About - Network" anywhere, but I found "About- UPS" with this info :
About your UPS / STS |
GALAXY 5000 60 kVA |
UPS / STS Name : |
GALAXY 5000 60 kVA
|
UPS / STS Firmware revision : |
KD.GDENB1S300IC303
|
Network Management Card |
Firmware revision : | KD (SN 49er35533) |
Posted: 2021-06-30 06:02 AM
This reply was originally posted by Gavan on APC forums on 9/29/2020
I believe you have a pre-APC card, the MGE SNMP Web Card - 66074 (KD revision)
https://www.se.com/ww/en/product/66074/mge-snmp-web-card/
The below FAQ has a video that you can use to confimr:
https://www.se.com/ww/en/faqs/FA281356/
-Gavan