Hi you
How to connect APC SMT 2200RMI2U to PC. I want recalibration battery
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:12 AM . Last Modified: 2 weeks ago
Hi Tuan,
You can connect to the UPS via Serial or USB using Powerchute Business Edition. If the UPS has a Network Management card installed, you can also connect to the UPS via a web interface. In addition, if you just want to perform a calibration, that can be done via the LCD screen on the front of the unit. Go to "Test and Diags" then choose "CalibrationTest". You will need at least 10% load attached to the UPS to initiate a calibration, and more load is better.
Thanks
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:12 AM . Last Modified: 2 weeks ago
Hi Tuan,
You can connect to the UPS via Serial or USB using Powerchute Business Edition. If the UPS has a Network Management card installed, you can also connect to the UPS via a web interface. In addition, if you just want to perform a calibration, that can be done via the LCD screen on the front of the unit. Go to "Test and Diags" then choose "CalibrationTest". You will need at least 10% load attached to the UPS to initiate a calibration, and more load is better.
Thanks
Liam