Hi,
I have an SUA1500i model APC UPS Purchased on 11th January 2013. In October 2015 it's backup time
reduced to 5 minutes. Upon inspection one of the internal battery was found to be down. Then I replaced
the Batteries with Amaron Quanta 12 V 18 AH Batteries( 2 No.s). Now next day after replacement suddenly
there was a Beep sound and the Battery Charge LED is showing the lowest charge level. Then the APC Dealer who
replaced the Battery says it has to be Calibrated and for that 9-port is required. How to calibrate and what is this port?
Is USB Port enough ? SUA1500i model UPS is having one serial port and one USB port. Please help. Thanks in advance.
Posted: 2021-06-30 11:08 PM
This was originally posted on APC forums on 11/26/2015
Hi Stuart,
Thanks a lot for the fast, detailed response. Sure it did help. Can I use a USB Cable instead of the serial cable?
Regards
Posted: 2021-06-30 11:08 PM
This was originally posted on APC forums on 11/25/2015
Hi Jayan,
First you could try a manual battery calibration.
1. Charge the batteries fro atleast 8 hours
2. Stop the PowerChute plus software from running and disconnect
the serial cable.
3. There must be at least a 30% load attached to the UPS during
this procedure, but the process will cause the UPS to shut off and cut power to
its outlets. Therefore, attach a non-critical load to the UPS and then force
the UPS on battery by disconnecting it from utility power. Allow the unit to
run on battery until it turns off completely. Make sure at least a 30% load is
present!
4. Plug the UPS back into the wall outlet and allow it to recharge (it
will recharge more quickly turned off and with no load present). Once the unit
has recharged, the ""runtime remaining"" calculation should be more accurate.
Hopefully this helps
Posted: 2021-06-30 11:08 PM
This was originally posted on APC forums on 11/26/2015
Hi Stuart,
Thanks a lot for the fast, detailed response. Sure it did help. Can I use a USB Cable instead of the serial cable?
Regards
Posted: 2021-06-30 11:08 PM
This reply was originally posted by Bill on APC forums on 11/26/2015
Jayan,
If you are following the procedure Stuart recommended you do not need either cable. If you are running PowerChute depending on the version you can use either USB or Serial.
Posted: 2021-06-30 11:08 PM
This was originally posted on APC forums on 11/27/2015
Hi Bill,
Thanks a lot. Now everything is clear. Here some unprofessional people were confusing by giving
wrong information by saying 9-port is required for running calibration etc.
I'm so glad that I have joined the A P C Forum. Thanks once again Bill and Stuart.