My company is installing a network system in a very remoter location and we must have 8 hours of backup battery power.
The backup system must be able to support the following:
One router: Power consumption is 160 w max and input current is 4A @ 110VAC
One switch: Power consumption is 148 w max and input current is 1.2A max
Five internet access devices: Power consumption for each is 1.2A 70W
Am I correct to say that the total maximum power requirements for the above system is 658 watts per hour? If so, what type of APC arrangement would met my needs?
Sorry, my user name is " LikeAPro", however, I am very new to this.
I would appreciate any help on this matter.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:13 AM . Last Modified: 2024-03-08 01:23 AM
Thanks!
A generator would be great, however this site location is extremely remote and getting a service tech there with a generator could take 6 to 8 hours.
Where I go to plug in the total watts and hours to come up with the sizing requirements?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:13 AM . Last Modified: 2024-03-08 01:23 AM
You can size based on your Watt values as long as they are Max values.
Generally speaking though, if you want 8 hours of backup, the common method would be to have a battery back-up to handle the initial power outage until a generator can kick in to supply extended runtime.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:13 AM . Last Modified: 2024-03-08 01:23 AM
Thanks!
A generator would be great, however this site location is extremely remote and getting a service tech there with a generator could take 6 to 8 hours.
Where I go to plug in the total watts and hours to come up with the sizing requirements?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:13 AM . Last Modified: 2024-03-08 01:23 AM
Hi,
I used the selector here and it provided some 120V matches.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:13 AM . Last Modified: 2024-03-08 01:23 AM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.