Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-26 02:45 AM
This was originally posted on APC forums on 4/14/2017
Hello all,
We have a galaxy 3000 ups that after a restart return charger fault and the battery cb goes off after 5 to 10 seconds of the startup.
The batteries are fully charged, each one reads between 13.3 and 13.5, the whole group reads 320v.
Any idea I appreciate.
Posted: 2021-06-26 02:45 AM
This reply was originally posted by Bill on APC forums on 4/14/2017
Luis,
I asked our Galaxy support team and they replied
Most likely he has an open battery or connection in his battery string.
They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.
Posted: 2021-06-26 02:45 AM
This reply was originally posted by Bill on APC forums on 4/14/2017
Luis,
I asked our Galaxy support team and they replied
Most likely he has an open battery or connection in his battery string.
They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.
Posted: 2021-06-26 02:45 AM
This was originally posted on APC forums on 5/24/2017
You need to measure the voltage of each battery separately, necessarily with a small load of 2-5 watts
User | Count |
---|---|
4835 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.